0 votes
45 views 0 comments
ago in Networks by

I have some RUT240 modems. Until firmware 1.11.3 I have no problem reading registers with modbus tcp. After upgrading to version 1.12.2 , every time I read a register it says "TCP/IP connection terminated". It read the value, but after show this error. Until fw 11.3, I didn't have this problem. I'm using "Modscan32" program, but also using Siemens plc I have the same problem, now.

Thank you

1 Answer

0 votes
ago by
Hello,

This is a know situation. Currently RnD works on fix, which will be released with next official firmware. For now downgrade router to firmware, which works for you and wait for next release.
Best answer