Hello,
I've tested your setup and everything seems to be working as expected. The router sends the GET or POST request to the specified server.
In one of your attached screenshots, I can see, that the "Add conditions" field is left blank. This should not be blank as the rule will not trigger without it.
If you want to trigger this rule when the Input pin is set to HIGH, then a condition is needed. Conditions can be configured in the I/O Juggler menu, Conditions tab:
- Create a name for the rule;
- Set I/O to Input;
- Set State to High;
Save the rule and navigate to the General tab. There, in the created rules, in the "Add conditions" field specify the rule you just created, and the action should be PLC on your setup.
Also, do not forget to add the created condition to the PLC rule, created in the Actions tab.
As an example, I'm attaching screenshots of how my setup looks like:
Created condition:
Created action:
Rule, created in the general tab:
Of course, make sure the I/O Juggler is enabled in the General tab.
Let me know if you're still experiencing issues.
Best regards,
DaumantasG