is it possible to use the rut955 as a Modbus TCP gateway. I have several Modbus RTU devices connected via RS485 to the Rut955. I would like to read out values from these RTU devices from my remote SCADA system.

I´ve just found an option to send the data via JSON File. This would be a push method.

Reading out the Rut955 via Modbus seems to be possible just for Router parameters, but not for connected slaves.

Greetings Chris
by
Hello, it's possible but be carefull, modbus deamon can crash randomly after a reboot of RUT :
See https://community.teltonika-networks.com/18434/rut955-rs485-modbus-gateway-crash-after-reboot?show=18434#q18434

3 Answers

0 votes
by
  • Set the port as Modbus Gateway on your rut (Example: LAN IP 192.168.1.1).
  • Ensure that all the RTU devices have unique ID (Address)
  • Request connection to 192.168.1.1 with the device ID for the address.
0 votes
by
Hi!

Yes, it's possible. In Services - RS232/RS485 section you can configure the Modbus Gateway.
0 votes
by
Thank you.

I will try it and come back with results. Also the rebooting issue is good to know about.

Greetings Chris