Hello,

is it possible to use the rut955 as a Modbus TCP gateway. I have several Modbus RTU devices connected via RS485 to the Rut955. I would like to read out values from these RTU devices from my remote SCADA system.

I´ve just found an option to send the data via JSON File. This would be a push method.

Reading out the Rut955 via Modbus seems to be possible just for Router parameters, but not for connected slaves.

Greetings Chris

2 Answers

0 votes
ago by
  • Set the port as Modbus Gateway on your rut (Example: LAN IP 192.168.1.1).
  • Ensure that all the RTU devices have unique ID (Address)
  • Request connection to 192.168.1.1 with the device ID for the address.
0 votes
ago by
Hi!

Yes, it's possible. In Services - RS232/RS485 section you can configure the Modbus Gateway.